A roof top unit(combination AC and gas heat) has a full load of 29 amps. Would a 30 amp fusible disconnect with time delay 30 amp fuses and # 10 wire be acceptable or would the 115% of 28-714 apply?
-
May 15th, 2003, 09:40 PM
#2
Inactive Member
Hello Ampacity,
Yes 28-714 does apply !
Also #10 wire is not large enough as 28-106 & 28-706 requires the conductors to have an ampacity not less than 125% of the motor FLA.
Also check out 28-708 for overcurrent device sizing.
Hope this helps..