    A roof top unit(combination AC and gas heat) has a full load of 29 amps. Would a 30 amp fusible disconnect with time delay 30 amp fuses and # 10 wire be acceptable or would the 115% of 28-714 apply?

  2. #2
    Inactive Member bigrockk's Avatar
    Join Date
    September 29th, 2002
    Posts
    146
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Hello Ampacity,

    Yes 28-714 does apply !

    Also #10 wire is not large enough as 28-106 & 28-706 requires the conductors to have an ampacity not less than 125% of the motor FLA.

    Also check out 28-708 for overcurrent device sizing.

    Hope this helps..